davezawadi

Posts: 4259
Joined: 26 June 2002
|
Hi Leckie
I do class all of those as dangerous, possibly only potentially dangerous. But this one is different and well beyond the content of this leaflet by a self proclaiming vested interest.
Bare conductors which are possibly within reach are not permitted. They are potentially dangerous, but not immediately dangerous. These should be coded as C1. These CUs have been deemed to be likely to be the cause of fires, which are potentially dangerous, but are not permitted either. An installation in a petrol station with inadequate Ex equipment is also only potentially dangerous. All of these should be coded as C1 because none of therm are permitted in Amdt3. This dangerous classification is simply a mechanism to allow often rather inadequately informed inspectors to give codings to domestic disasters such as cracked sockets, cables hanging off the walls, unearthed metal lampholders etc.
Inadequately low Zs, incorrect cables sizes etc. are serious defects with potentially serious consequences, either electric shock due to extended disconnection time or fire. The ESF have forgotten that all circuits do not have RCDs, or that overloaded cables get very hot after a period. Fires are always very serious indeed, fumes are often lethal even if someone is not burned. These seem to be considered C2 by ESF, whereas it depends on the exact circumstances, a 1.5mm cable feeding a 12kW shower (yes I have found this) is a C1, as is a Zs of 10 ohms for a ring circuit with no RCD present.
This is a toy leaflet directed at inexperienced domestic installers who dare to do a EICR. In my view it is representative of the quality of the ESF and all the other offshoots of vested interests which are bringing the industry into disrepute. It has all of the experience of a non-inspector of the inexperienced kind written all over and throughout its contents.
I am expecting the ESF to come out with a document saying that prohibited items are perfectly fine as long as they complied with a previous version of the regs. This is not the inspection standard! Prohibited items must be coded as though it were a new installation to the current regulations otherwise the whole process is flawed and redress may be available against the inspector if an incident occurs (and they do at one a day according the the fire service). As inspector you have a duty of care which you must take seriously or face prosecution under the HSAW act. Failure to realise a publicised danger, such as this, could lead to bankruptcy and prison very easily. Until there are a few test cases, you won't know but coroners keep taking a very serious attitude to cases like this and recommend prosecution. Look what has happened in one or two gas cases which are fairly similar in outcomes.
You should be aware that I think that this CU business is fully flawed, that evidence is very weak and that much more investigation by fully competent forensic engineers is required. Unfortunately we have to operate according to the regulations even if they are not to our liking, and are a knee jerk reaction to an unverified claim.
-------------------------
David BSc CEng MIET
|
leckie

Posts: 4705
Joined: 21 November 2008
|
Well I agree that the BPG's are all just guides, and different situations call for differents codes. This is rather a long thread and I have only just scanned through the various comments and opinions. I assume your position is that WHEN the new regulation is in place, and you are carrying out an EICR, that you will be giving a C1 for plastic consumers units that you find installed. So that would be nearly every dwelling in the country. Well I think we had best wait for the regulation to be put in writing in the new book and see how the industry, insurers, HSE, etc interpret the requirements before we start reaching any firm conclusions.
Regarding general codes for other items on EICR's, I think giving C1 or C2 to items should be done with great care. Claims for unnecessary cost incurred due to over zealous codes may affect PI just as much as being to lenient.
|
leckie

Posts: 4705
Joined: 21 November 2008
|
Also, I'm not sure referring to petrol filling stations is really a fair comparison to make. The electrical inspection and testing of filling stations is covered in the "blue book" and I wouldn't imagine many contractors carrying out domestic EICR's would be carrying out Periodic Inspections to a filling station.
|