If testing had been carried out properly would it have picked up this fault?
If the screw just clipped the live conductor on it's way into the metal studwork, thereby connecting the two together, how would any of the insulation tests we usually do show this?
In this particular case, JP reported that the c.p.c. had been blown away by the fault - suggesting that the screw initially hit L + c.p.c. - so even the simplest of insulation test should have spotted that.
It could very easily have been different though - as you suggest I doubt an insulation test would spot a screw into L alone, and the outcome could have been identical.
Similarly the Danny Edwards case where L & c.p.c. had been reversed at the socket - had the socket been on a radial, the normal "R1+R2" test as frequently taught wouldn't have spotted the problem before energization.
The courts and public have this quaint idea that testing will find any fault - while the real world is often a little less perfect (just ask any software developer).
I think we might be able to do better though. In the case of screws through hidden cables, it seems to me that the 'double insulation' approach is flawed as it clearly isn't robust enough for service conditions (people will put nails & screws into walls where they want, regardless of any 'safe zones' we might dream up). So the obvious alternative is real ADS - i.e. put earthed metal between the live conductors and any potential victims. MICC, SWA or steel conduit - or my current favourite at the moment - BS 8436 cables. I see it as catching the problem as it happens, not hoping to catch it at some later date when some poor victim completes the circuit to earth and hoping the RCD has been exercised recently. At the very least BS 8436 cable makes the insulation test viable again.
- Andy.