I understand the need for earthing.
Good
All circuits are earthed and the main earthing conductor completes the earthing of the circuits. The part where I disagree is bringing extraneous-conductive-parts in to the electrical system by placing bonding conductors on them.
Think about that again - if they are extraneous, they already have a potential (usually earth potential) - if you touch a metal item with an earth fault and that extraneous conductive part at earth potential you experience a touch voltage - it's what we used to call an indirect contact shock.
If I bond that conductor to the MET the fault causing the aplliance case to rise in voltage also pulls up that extraneous part and the voltage between the parts (ie the touch voltage experienced by the person is reduced
It is pure theory is it not that this earthing system comprising of earth, main bonding and supplementary bonding makes parts that would not otherwise be part of the electrical system safer if they do inadvertently acquire a voltage through a fault.
It most certainly is not theory - it a physical fact - ohms law dictates it
It is a well known fact that CURRENT causes death not VOLTAGE.
LoL - you'll be telling me next that "it's the volts that jolt but the mills that kill" - it is incredibly difficult to seperate the amps from the volts when you have a resonably fixed impedance like a human body
OK - if you want to be a pedant, if I apply a voltage to an impedance, then we will have current - the value of current being dictated by the voltage and the impedance combination. As the human body impedance is broadly fixed, then less or more voltage means less or more current - ohms law again.
A voltage can be present on something but current will only flow if a circuit can be made.
Indeed, the human body has impedance so the circuit is always made if only by capacitive coupling - why do you think we have limits on systems like Medical IT arrangements that are protecting from micro shock - in those kind of cases we are taking about perhaps a few milliamps in a suppressed patient being fatal
50mA of current is sufficient to kill.
It's a lot less than that actually - depends on the person and where we apply it - a few mills will do the job once we are through the skin - don't forget the human body is just a resonably tough bag containing lots of conductive fluids
Merely touching a live part if no current can flow will not kill you but you will get a painful shock if the voltage is big enough.
You would need to be very highly insulated for no current to flow - and that's not practicable in reality. I suspect Emma Shaw was already experiencing some current flow before she touched earthy metalwork
Seriously, you need to research and understand the touch voltage concept - because if you let your current thinking drive your design approach regarding bonding of extraneous conductive parts (or not in your case) then that is truly dangerous.
Do not let a little knowledge cause you a problem- take the time to understand the basic science behind the reasons for earthing and bonding - trust me, they are rooted in good science
Regards
OMS
-------------------------
Let the wind blow you, across a big floor.