I agree with you OMS about earthing everything in sight, but as I think there was probably very little possibility of detecting this fault once the power was applied, we have an impasse. You could say RCD everything, but that is not the answer because this is not a case where additional protection is indicated. It is a basic workmanship issue true, but any wiring inside this kind of partition is in danger from the construction screws even if it is in the "safe zones". As wiring inside stud walls is rarely fixed, at least in my experience, the zones are not very relevant, and they are bound to have fixing screws anyway.
However the discussion has moved away from what I consider to be the important matter, that is the practices of supposedly "approved" contractors. This case (and many many less serious ones, in outcome at least) show that the QS system is fatally flawed in that it is totally open to abuse and fraud. The unqualified tester appears to be used in flagrant breach of the EAWR by his employer and supervisor. The QS may have been under pressure to issue certs by the same employer. What has happened to the employer? Someone suggested he got a pat on the head from the approval body.
And this works, as in Part P I assume?
Another point you might like to try Andy, BS8436 cables do not prevent this problem because the contact cross section of the foil is very small and may well just burn away before the CPD opens. They are intended for fire resistance and electrical screening.
http://www.batt.co.uk/products...Tube/LSZH-Cable-BS8436
-------------------------
David
BSc CEng MIET