Topic Title: SPDs for a Church?
Created On: 27 February 2019 07:11 pm
yellowvanman
Rural Church - risk calculation <1000. Spire but no Lighting protection.
Nothing of any value (electrically) within - does it really need SPDs?
 27 February 2019 07:23 pm
Zoomup
Is it a heritage status building?
Z.
 27 February 2019 07:46 pm
yellowvanman
NO
 27 February 2019 08:40 pm
You`d think the C E O would prevent such acts of god occouring there
 27 February 2019 09:30 pm
chrispearson
No, but it may need lightning protection. Remember York Minster?
What might be fried in a rural church? The boiler controls? The sound system?
 28 February 2019 04:25 pm
yellowvanman
No Boiler, no sound system. Some lights and some infra red heaters thats about it!
 28 February 2019 05:30 pm
ArduinoXR
Risk assessment. No danger to life, no critical systems. Possibly a surge arrest on the MSB/Incoming. Only if asked for by the client after you have presented your opinion (as per above).
 28 February 2019 06:01 pm
What about an organ? Some of these can be very expensive instruments.
 28 February 2019 09:21 pm
chrispearson
No boiler etc. - the organ may still be hand-pumped.
 01 March 2019 12:21 pm
Angram
AS a matter of interest the York Minster fire was caused by lighting wiring being installed in a roof space when there was lightning conductor cable on the roof above: the lightning side flashed through the roof to the new lighting wires inside. The roof smouldered undiscovered until it was too late.
My friend from, then, Yorkshire Water, who was a lighting chaser saw the event.
Angram
 02 March 2019 12:59 am
wallywombat
Unless it's single dwelling, the "negligible value" exemption doesn't apply. Since CRL < 1000, that means that a rewire must include SPDs in order to comply with BS7671:2018. Whether you have to install SPDs for a job that is less than a complete reinstall is of course something that can be happily debated on forums without ever reaching a conclusion.
 02 March 2019 09:40 pm
Presuming a conventional organ, these use low pressure compressed air from a blower worked by a standard induction motor.
These motors are not particularly vulnerable and are cheap to replace.
As has already been said, a REALLY basic organ might use hand or foot powered bellows.
Exceptionally, small water turbines have been used.
 04 March 2019 06:29 am
Originally posted by: broadgage
. . . Presuming a conventional organ, these use low pressure compressed air from a blower worked by a standard induction motor.
These motors are not particularly vulnerable and are cheap to replace. . .
True, but it also depends on the link between the keys and the pipes. These could be mechanical or more often electro-pneumatic, where a small solenoid valve opens the air supply to each pipe. The small wiring in these can be quite significant.