Topic Title: Extending earth bonding
Topic Summary:
Created On: 19 April 2017 01:04 pm
Status: Read Only
Linear : Threading : Single : Branch
 Extending earth bonding   - goldenboy1818 - 19 April 2017 01:04 pm  
 Extending earth bonding   - dustydazzler - 19 April 2017 01:32 pm  
 Extending earth bonding   - geoffsd - 19 April 2017 01:41 pm  
 Extending earth bonding   - weirdbeard - 20 April 2017 06:53 pm  
 Extending earth bonding   - mapj1 - 19 April 2017 02:08 pm  
 Extending earth bonding   - John Peckham - 19 April 2017 04:41 pm  
 Extending earth bonding   - geoffsd - 19 April 2017 05:03 pm  
 Extending earth bonding   - geoffsd - 19 April 2017 06:52 pm  
 Extending earth bonding   - mapj1 - 20 April 2017 12:25 am  
 Extending earth bonding   - geoffsd - 20 April 2017 01:04 am  
 Extending earth bonding   - spinlondon - 19 April 2017 09:22 pm  
 Extending earth bonding   - AJJewsbury - 19 April 2017 10:11 pm  
 Extending earth bonding   - mapj1 - 20 April 2017 01:38 am  
 Extending earth bonding   - geoffsd - 20 April 2017 05:17 pm  
 Extending earth bonding   - geoffsd - 20 April 2017 07:07 pm  
 Extending earth bonding   - weirdbeard - 20 April 2017 07:22 pm  
 Extending earth bonding   - geoffsd - 20 April 2017 07:28 pm  
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 19 April 2017 06:52 pm
User is offline View Users Profile Print this message



geoffsd

Posts: 2342
Joined: 15 June 2010

I have found this in the same part of BS7430;

"The bonding connections to the water and gas pipes
should be made as near as possible to their point of
entry into the premises. If there is an insulating
section or insert at that point, the bonding
connection should be made to the metallic pipes on
the consumer's side of the section or insert."


Same poor practice as 544.1.2

It continues:

"The main equipotential bonding connections to the
main water pipes should normally be on the
consumer's side of the stop tap"


Why?

"but connection on the
Water Authority's side of the stop tap is acceptable,
as long as there is satisfactory electrical continuity
across the tap
."


It doesn't inspire confidence, does it?


Edit - From 1998 edition.

Edited: 19 April 2017 at 07:25 pm by geoffsd