 25 January 2019 06:55 PM
|
Bewlec

Posts: 34
Joined: 11 June 2017
|
This will be a quick one for most of you, but trying to work out the minimum acceptable size of the main earthing conductor.
TNS supply protected by 60Amp fuse ( Not Verified as sealed ), measured pfc of 1.80kA.
At present it is connected onto the lead sheath via what looks to be an approx 2.5mm bare conductor.
I calculate this at 3.98mm, but not sure if my sums are correct, any advise is appreciated. Thanks
Edited: 25 January 2019 at 07:42 PM by Bewlec
|
|
|
 25 January 2019 08:37 PM
|
Zoomup

Posts: 6117
Joined: 20 February 2014
|
Is the earthing conductor tinned copper and stranded and soldered onto the lead sheath?
Z.
|
|
|
 25 January 2019 08:46 PM
|
Bewlec

Posts: 34
Joined: 11 June 2017
|
Definitely soldered onto sheath, but not 100% sure if it's tinned copper or not
|
|
|
 25 January 2019 08:57 PM
|
Zoomup

Posts: 6117
Joined: 20 February 2014
|
Taking t as 0.01s, and k as 159 (table 54.6) I make S at just over 1.1mm2, which seems far too small. I will be interested in finding the correct answer though. The final temperature of the copper conductor will be 200 degrees though.
Z.
Edit bad arithmetic.
Edited: 25 January 2019 at 09:04 PM by Zoomup
|
|
|
 25 January 2019 09:06 PM
|
Zoomup

Posts: 6117
Joined: 20 February 2014
|
I am basing t on 0.01s with a B.S. 1361 60 Amp fuse.
Z.
|
|
|
 25 January 2019 09:09 PM
|
Zoomup

Posts: 6117
Joined: 20 February 2014
|
Of course it may well be a TN-C-S supply in the road and just presenting as a TN-S supply in the premises. In which case table 54.7 might best be used.
Z.
|
|
|
 25 January 2019 09:25 PM
|
Bewlec

Posts: 34
Joined: 11 June 2017
|
I have used table 54.2. Bare conductor in contact with cable covering as soldered onto sheath but cable has a wrap of some sort around it. Also I used 0.1 seconds as this is the lowest available on the curve characteristics for 1361 60amp. Like mentioned I'm not sure these are the correct entries to use.
|
|
|
 25 January 2019 10:15 PM
|
UKPN

Posts: 718
Joined: 17 January 2012
|
This is a DNO situation.16mmsq reqd.
Regards, UKPN.
Edited: 25 January 2019 at 10:42 PM by UKPN
|
|
|
 25 January 2019 10:22 PM
|
chrispearson

Posts: 1095
Joined: 15 February 2018
|
Any chance of a photo?
|
|
|
 26 January 2019 12:10 AM
|
mapj1

Posts: 12039
Joined: 22 July 2004
|
The modern way is a flat braid and a constant force spring, as hot works are now considered dangerous. If it needs replacing its really a call to the DNO.
But the Adiabatic eqn., well lets assume we start at 30c and the lead tin solder is soft solder and melts at 200c
(235 is a good no to remember, both for uranium (atomic mass) and for most solders being soft, including the higher lead fraction ones, and the modern lead free stuff. we had a tech who used to set all the soldering tools for what he called a "uranium run" when we switched to lead free in the mid 2000s.)
where the '2' denotes a square
I2t<=K2S2
S is the minimum protective conductor cross-sectional area (mm2)
I is the fault current (A)
t is the opening time of the protective device (s) now that is tricky - the curves go to 0.1 sec normally, and then it is "see maker's data"
page 26 here suggests 900A and 0.01 seconds for a 60A fuse.
if it got no faster, so 0.01s* 1800A*1800A
k is a factor depending on the conductor material and insulation, and the initial and maximum insulation temperatures. take k= 160
for 30 to 200C
page 26 here suggests 900A and 0.01 seconds for a 60A fuse.
if it got no faster, so 0.01s* 1800A*1800A, so I2t is 32400 amps squared per second.
So S= root of that divided by k 2
32400 /(160*160) = 1.22 mm2, so S= 1.125mm.
But really you need more info, if anyone on the substation has PME, as there may be unfused and therefore very long duration currents between plumbing and the CPC, that are not coming via your company fuse over which you have little control.These diverted neutral currents can overheat inadequate earthing arrangements.
-------------------------
regards Mike
|
|
|
 26 January 2019 03:14 PM
|
Timeserved

Posts: 146
Joined: 18 October 2016
|
So S= root of that divided by k 2
543.1.3 shows that it's divided k and not k squared.
But I would use table 54.7 in this case.
I normally only use the adiabatic equation if I'm calculating submain CPC size.
Either way I would welcome someone to confirm if I'm correct or if it's a typo in the big blue book.
Cheers
Ts
|
|
|
 26 January 2019 08:41 AM
|
Zoomup

Posts: 6117
Joined: 20 February 2014
|
UKPN is correct. Please see above.
Z.
|
|
|
 26 January 2019 08:53 AM
|
UKPN

Posts: 718
Joined: 17 January 2012
|
Thank you Zoomup, have a good weekend.
Regards, UKPN.
|
|
|
 26 January 2019 03:41 PM
|
Zoomup

Posts: 6117
Joined: 20 February 2014
|
543.1.3
Multiply I squared by t, then find the square root of that number. Then divide that answer by k. That will give you S.
Z.
Edit. Corrected for bad eyes' error.
(Don't get confused with I2t<=k2S2)
Edited: 26 January 2019 at 03:55 PM by Zoomup
|
|
|
 27 January 2019 01:29 AM
|
Timeserved

Posts: 146
Joined: 18 October 2016
|
Thanks Z, I'm happy I'm doing this correctly. ??
|
|
|
 27 January 2019 08:11 AM
|
lyledunn

Posts: 1228
Joined: 13 August 2003
|
It would be inappropriate to have the earthing conductor selected using a method which depends on another authority. The situation is one where the requirements of the DNO must be met.
-------------------------
Regards,
Lyle Dunn
|
|
|
 27 January 2019 03:18 PM
|
alanblaby

Posts: 868
Joined: 09 March 2012
|
Originally posted by: lyledunn
It would be inappropriate to have the earthing conductor selected using a method which depends on another authority. The situation is one where the requirements of the DNO must be met.
Yes, but in the case of the OP, he thinks the DNO soldered connection to the sheath is too small. In that case he cannot do anything without DNO involvement, who will probably not do anything about it. (Using the equation, shows it may well be fine anyway)
However, I think our responsibility starts (our earthing conductor) at the connection joint to this soldered conductor from the sheath, and from that point we need our 10/16/25mm earth conductor cable to our installation.
|
|
|
 27 January 2019 04:13 PM
|
Bewlec

Posts: 34
Joined: 11 June 2017
|
The reason I am asking if the equation is correct is because this forms part of a domestic condition report and therefore I need to confirm that the earthing conductor is of an acceptable size and code it accordingly.
I know that if undersized, it is a matter for the DNO and I would not attempt to up grade the conductor myself.
Thanks.
|
|
|
 27 January 2019 08:49 PM
|
UKPN

Posts: 718
Joined: 17 January 2012
|
This is a SNE earthing facility which is available for the consumer if he chooses to use it. The DNO have no responsibility that is the consumers. Probably a 60/70s sheath, with the old 7.029 cable, around 20 amp. One second rating, 275 amp. Best to sleeve the bare cable, fit an earth block if not already, give us a ring and we will deal with it. We may PME the service, so bonding must be to the ESQCR regs. Hope this helps.
Regards, UKPN.
|
|
|
 28 January 2019 09:55 AM
|
chrispearson

Posts: 1095
Joined: 15 February 2018
|
Originally posted by: Bewlec
I calculate this at 3.98mm, but not sure if my sums are correct, any advise is appreciated. Thanks
Is there only one strand? If a piece of copper wire has been wrapped around the sheath, there ought to be at least two ends.
|
|
|
 29 January 2019 03:54 PM
|
Zoomup

Posts: 6117
Joined: 20 February 2014
|
I've only ever seen a tinned copper braid, like a car earthing lead from the battery to the chassis, or a 3 or 7 stranded tinned copper earthing lead/earthing conductor soldered onto the lead sheath of a P.I.L.C. cable, never just one single strand. I can only imagine that the single strand has been installed by a D.I.Y.er or that the installation is so old that it initially just had a few lights only.
Z.
|
|
|
 29 January 2019 05:35 PM
|
Bewlec

Posts: 34
Joined: 11 June 2017
|
It's a stranded cable, soldered onto sheath then connected to MET on cutout board, but not sure on number of cores off the top of my head, but going back this weekend to sort other faults so I'll confirm back then. As UKPN mentions, it is probably 7.029 as I thought it was approx 2.5mm.
|
|
|
 29 January 2019 05:56 PM
|
chrispearson

Posts: 1095
Joined: 15 February 2018
|
Originally posted by: Bewlec
It's a stranded cable, soldered onto sheath then connected to MET on cutout board, but not sure on number of cores off the top of my head, but going back this weekend to sort other faults so I'll confirm back then. As UKPN mentions, it is probably 7.029 as I thought it was approx 2.5mm.
If it's like mine, it is two strands of 4 sqmm (2.25 mm diameter), which with both ends makes 16 sqmm overall. I have to say, that it doesn't look like much, but I have checked it.
|
|
|
 29 January 2019 06:22 PM
|
Zoomup

Posts: 6117
Joined: 20 February 2014
|
That looks like three conductors twisted together Chris.
Z.
|
|
|
 29 January 2019 08:11 PM
|
Bewlec

Posts: 34
Joined: 11 June 2017
|
Similar Chris, but it is not as thick. Imagine stripping some 7.029 from an old socket circuit and that's the approx size.
How do you add photos?
|
|
|
 29 January 2019 08:26 PM
|
AJJewsbury

Posts: 17795
Joined: 13 August 2003
|
How do you add photos?
This forum won't host photos for you - you need to upload them somewhere else on the internet that's public, then link to them (e.g. using the  button in the reply box). (Or if it's a big picture, just include a simple link to the picture in your post - that way the layout won't get messed up and we won't have to suffer useful things being obscured by the adverts)
The new Forum is far better is that respect (you can upload all kinds of images and files into your own folder and then reference then in as many posts as you like) - indeed you could upload them into the new Forum and then link to them to a post here in the old Forum with a bit of effort.
- Andy.
|
|
|
 29 January 2019 09:37 PM
|
mapj1

Posts: 12039
Joined: 22 July 2004
|
The modern way is not solder but these things - constant force springs used in conjunction with flat multi-strand braid which gets squished by the small force from each of several turns of the spring.
Not for us to put them on DNO cables of course, but handy for pipework in situations where the BS951 type clamp is likely to get shaken off or not make good contact, or lead pipes and cable armours of odd sixes. I have used them to make contact to the braid of a very chunky coax cable part way along for example (and then covered back in with self amalgamating tape.)
Fitting them is a bit of a knack, as they combine the twang of clock spring and the sharp edge of a freshly opened tin can, so some practice is needed.
-------------------------
regards Mike
|
|