Topic Title: Fuses in IEC leads
Topic Summary: What is the maximum fuse rating for an IEC lead?
Created On: 29 May 2009 11:08 AM
Status: Read Only
Linear : Threading : Single : Branch
 Fuses in IEC leads   - RobinBarton - 29 May 2009 11:08 AM  
 Fuses in IEC leads   - AJJewsbury - 29 May 2009 10:41 PM  
 Fuses in IEC leads   - timjames2 - 30 May 2009 12:10 AM  
 Fuses in IEC leads   - gkenyon - 30 May 2009 02:08 PM  
 Fuses in IEC leads   - perspicacious - 30 May 2009 04:04 PM  
 Fuses in IEC leads   - davyn1 - 30 May 2009 05:50 PM  
 Fuses in IEC leads   - timjames2 - 31 May 2009 12:05 AM  
 Fuses in IEC leads   - timjames2 - 31 May 2009 12:26 AM  
 Fuses in IEC leads   - gkenyon - 03 September 2009 05:14 PM  
 Fuses in IEC leads   - davyn1 - 31 May 2009 08:32 AM  
 Fuses in IEC leads   - Baz - 31 May 2009 02:14 PM  
 Fuses in IEC leads   - perspicacious - 31 May 2009 02:58 PM  
 Fuses in IEC leads   - alancapon - 31 May 2009 03:50 PM  
 Fuses in IEC leads   - Angram - 03 September 2009 10:32 PM  
 Fuses in IEC leads   - perspicacious - 03 September 2009 11:02 PM  
 Fuses in IEC leads   - gkenyon - 04 September 2009 09:34 AM  
 Fuses in IEC leads   - sparkingchip - 06 September 2009 11:57 AM  
 Fuses in IEC leads   - sparkingchip - 06 September 2009 12:03 PM  
 Fuses in IEC leads   - sparkingchip - 06 September 2009 12:16 PM  
 Fuses in IEC leads   - gkenyon - 06 September 2009 02:58 PM  
 Fuses in IEC leads   - Angram - 06 September 2009 02:38 PM  
 Fuses in IEC leads   - sparkingchip - 06 September 2009 03:07 PM  
 Fuses in IEC leads   - anastasis - 06 September 2009 03:17 PM  
 Fuses in IEC leads   - sparkingchip - 06 September 2009 03:18 PM  
 Fuses in IEC leads   - sparkingchip - 06 September 2009 04:39 PM  
 Fuses in IEC leads   - sparkingchip - 06 September 2009 04:46 PM  
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 29 May 2009 11:08 AM
User is offline View Users Profile Print this message



RobinBarton

Posts: 6
Joined: 07 November 2002

If you have a lead with a 13A plug and an IEC socket (which is rated at 10A), surely the maximum rating of fuse in the plug is 10A as a large proportion of IEC inlets are not fused. A lead with a 13A fuse should, surely, fail a visual inspection?

Am I wrong?

I queried this with my supplier (as their leads are all supplied with 13A fuses). Their response was that it is to do with inductive loads and the associated inrush current. I cannot work this one out myself - surely a 10A BS1362 fuse would withstand the inrush of most 10A inductive loads.

If I install a 32A 60309 outlet on a wall - I have to protect it with a 32A breaker, regardless of the load (although I can choose the breaker type with respect to inrush currents etc). So how come these leads can be supplied with 13A fuses...?